BS 7671 Section 521.8.3
Section 521.8.3 of BS7671 states: Where two or more circuits are terminated in a single junction box this shall comply with BS EN 60670-22. My question is what if several circuits will terminate in a single wiring device back box which are usually  manufactured to comply with   BS EN 60670-1.
Parents
  • I agree that there seems to have been a drift in the language over the years - originally a circuit was the entire loop, starting at the source of voltage, so conceptually you had many overlapping circuits - the lighting circuit started at the substation, passed over the DNO's wires, through the meter, out through way 6 of the CU and the lighting cables to the furthest light. The shower circuit shared the same path until way 1. The bit after the CU fuse was designated a ‘sub-circuit’.
    Somewhere along the lines we dropped the ‘sub-’ bit from the name, so now when we refer to a circuit we're really just referring to a sub-circuit.
    I don't see the term way catching on instead of (sub-)circuit though - ‘the upstairs lighting way’? No-one will know what I'm talking about… (I know, what's new there you say…)