Zs and Ipfc
Hi guys,
I have got measured Zs and Ipfc at a 3-phase distribution board from the EICR, but have no information of all upstream equipment including cable lengths/ sizes from the 230V source.
To my understanding, there's no way I can derive the voltage drop up to that DB from Zs/ Ipfc because I'll need the earth-fault current  or phase-phase impedance. Am I correct?
Second question is: In the same case, say a 1-phase load is supplied by this distribution board, and i'd like to know the prospective short circuit current to check against the disconnection time of the circuit breaker.
The pscc at the load end cannot be calculated as well because i'll need to know the voltage at the load and total loop impedance?
Thanks!
  • If it is impossible to test the voltage/loop etc at the source, then do your requisite checks at the remote DB. This is a common occurence in industrial premises, where you cannot turn off the power to do a dead test.
    The supply should be 230v +10%/-6%. See what you have at the DB, then use that figure to calculate your final circuits.
    For the single phase DB, the same applies, if you cannot dead test it, you can do a Live test, and use those figures. If it is an ‘always live’ circuit, you may need to do a number of tests at different hours to ensure that connected loads are not unduly influencing your test results.
  • Whats an IPFC? I noticed a few of these odd extra letters creeping in more and more often
  • To my understanding, there's no way I can derive the voltage drop up to that DB from Zs/ Ipfc because I'll need the earth-fault current  or phase-phase impedance. Am I correct?
    Ohm's Law relates voltage, impedance and current - so given one (impedance or current) and a decent assumption about the second (voltage) you should always be able to calculate the 3rd (current or impedance). Always take care to make sure you understand which ‘loop’ in involved and so which conductors the impedance relates to. For a 3-phase system the max PFC almost certainly relates to a bolted 3-phase (L-L-L) fault - so that in effect gives you the impedance of one of the line conductors (with Uo across it).
    You might have to make some assumptions - such as the impedance of the N conductors is similar to that of the L ones - which may be reasonable for a modern installation, but could be out  for a much older one where reduced neutrals were common. But still you should be able to get some numbers that should be useful enough to suggest whether you're in the right general area or not.
    That's not the whole story of course - when those values generally relate to the entire loop, and when it comes to voltage-drop you're usually only concerned with the part within your installation, and not about the part of the loop within the DNO's cables. If you're on a large site with its own HV transformer then it probably makes next to no difference, but even on a small domestic you should still be able to work out some ‘worst case’ values - and if they're sufficient to show your design is OK, then happy days.
    Of course, most common loop impedance meters have less than perfect accuracy anyway - many can give readings several tens of percent different from a true value and still be within calibration, especially on relatively low impedance loops, so such readings need to be taken with large pinch of salt.
    Quite correct - it should either be the symbol Ipf (current, prospective fault) or the abbreviation PFC (prospective fault current). (I think) I knew when the OP meant though.
  • Thanks aj that makes it all nice and clear
    Thanks all and sorry for the confusion with the abbreviations.