Yes a 2.5mm2 T&E cable can supply a 7,300 Watt instantaneous water heater at 240 Volts. I came across this today. The supply was from a B32 M.C.B. So why do we use bigger cable than 2.5mm2 if it will do the job?
The run was about 5m maximum.
Z.
AJJewsbury:
Zoomup:
Perhaps the pointed headed men in white coats at the I.E.T. could consider a Cfut correction factor. We already have Ca, Cc, Cd, Cf, Cg, Ci, Cs to name but a few.
Cfut cold refer to the functional utilisation time conditions. So, if applied, it would allow a large load to be supplied by an otherwise inadequately sized cable, but only for a short period of time, before the cable becomes dangerously hot and starts smoking. This approach will save materials and money.
Z.
No need - the concept is already in BS 7671 - see 533.2.1 3rd paragraph (although done by adjusting the design current rather than by a correction factor).
- Andy.
533.2.1 3rd paragraph is concerned with choosing the values of In and I2 surely. I was concerned with the duty cycle of a cable. Say it is overloaded by 30 percent for short periods, say 10 percent of its operational time, would it really suffer?
Z.
AJJewsbury:
Zoomup:
Perhaps the pointed headed men in white coats at the I.E.T. could consider a Cfut correction factor. We already have Ca, Cc, Cd, Cf, Cg, Ci, Cs to name but a few.
Cfut cold refer to the functional utilisation time conditions. So, if applied, it would allow a large load to be supplied by an otherwise inadequately sized cable, but only for a short period of time, before the cable becomes dangerously hot and starts smoking. This approach will save materials and money.
Z.
No need - the concept is already in BS 7671 - see 533.2.1 3rd paragraph (although done by adjusting the design current rather than by a correction factor).
- Andy.
533.2.1 3rd paragraph is concerned with choosing the values of In and I2 surely. I was concerned with the duty cycle of a cable. Say it is overloaded by 30 percent for short periods, say 10 percent of its operational time, would it really suffer?
Z.