Yes a 2.5mm2 T&E cable can supply a 7,300 Watt instantaneous water heater at 240 Volts. I came across this today. The supply was from a B32 M.C.B. So why do we use bigger cable than 2.5mm2 if it will do the job?
The run was about 5m maximum.
Z.
very very roughly, with ambient temp 30 degrees, with a 32 A load after a few minutes use (up to 5 mins but may be less):
- Ref method C (clipped direct) get to about 80 deg C
- Ref method 102# gets to about 90 deg C
- Ref method 103# gets to well over 100 degrees C
What's the assumed initial conductor temperature?
GN 6 (at least my ancient copy) suggests 15min for 2.5mm2 when considering 'duration of load current for equivalent constant load' - suggesting to me at least that a cable would take around that long to get to 70 degrees from cold (ambient) - so I'd expected significantly longer again to 80/90/100 degrees from cold.
- Andy.
very very roughly, with ambient temp 30 degrees, with a 32 A load after a few minutes use (up to 5 mins but may be less):
- Ref method C (clipped direct) get to about 80 deg C
- Ref method 102# gets to about 90 deg C
- Ref method 103# gets to well over 100 degrees C
What's the assumed initial conductor temperature?
GN 6 (at least my ancient copy) suggests 15min for 2.5mm2 when considering 'duration of load current for equivalent constant load' - suggesting to me at least that a cable would take around that long to get to 70 degrees from cold (ambient) - so I'd expected significantly longer again to 80/90/100 degrees from cold.
- Andy.