Yes a 2.5mm2 T&E cable can supply a 7,300 Watt instantaneous water heater at 240 Volts. I came across this today. The supply was from a B32 M.C.B. So why do we use bigger cable than 2.5mm2 if it will do the job?
The run was about 5m maximum.
Z.
AJJewsbury:
533.2.1 3rd paragraph is concerned with choosing the values of In and I2 surely.
Read it again… ".. based on values of Ib and Iz for the thermally equivalent constant load".
- Andy.
I have read it several times. It assumes a constant load with no consideration of duty cycles as my previous observations mentioned.
Z.
AJJewsbury:
533.2.1 3rd paragraph is concerned with choosing the values of In and I2 surely.
Read it again… ".. based on values of Ib and Iz for the thermally equivalent constant load".
- Andy.
I have read it several times. It assumes a constant load with no consideration of duty cycles as my previous observations mentioned.
Z.