Whenever transitioning from a preceding supply cable protected by a higher current circuit breaker or fuse, I always fuse down before connecting the appropriate lower gauge wire.

 

What I wonder is then how such distribution blocks like these Weidmüller AWPD 35 4X6/6X2.5 are safe:

 

336b015b6f6025bb0464050c14dff2fc-huge-weidmuller-awpd-35-4x6-6x2-5.png
35mm² to 2.5mm²
Parents
  • Former Community Member
    0 Former Community Member

    What I wonder is then how such distribution blocks like these Weidmüller AWPD 35 4X6/6X2.5 are safe:

    They don't appear to be any different to thousands of bus-bar chambers at 400 A with 16 mm2 cable off the bar to the switch-fuse adjacent.

    They rely on the integrity of the installer to provide a suitable protective device on the outgoing circuit.

    Or, if you're looking at DNO world, there may be a 300 mm2 cable backed up with a 400 A fuse with 35 mm2 connected to it! The cable is protected from overload by the 80 A fuse in your cut-out (see 433.2).

    Regards

    BOD

Reply
  • Former Community Member
    0 Former Community Member

    What I wonder is then how such distribution blocks like these Weidmüller AWPD 35 4X6/6X2.5 are safe:

    They don't appear to be any different to thousands of bus-bar chambers at 400 A with 16 mm2 cable off the bar to the switch-fuse adjacent.

    They rely on the integrity of the installer to provide a suitable protective device on the outgoing circuit.

    Or, if you're looking at DNO world, there may be a 300 mm2 cable backed up with a 400 A fuse with 35 mm2 connected to it! The cable is protected from overload by the 80 A fuse in your cut-out (see 433.2).

    Regards

    BOD