Terminal blocks - no fusing down?

Whenever transitioning from a preceding supply cable protected by a higher current circuit breaker or fuse, I always fuse down before connecting the appropriate lower gauge wire.

 

What I wonder is then how such distribution blocks like these Weidmüller AWPD 35 4X6/6X2.5 are safe:

 

336b015b6f6025bb0464050c14dff2fc-huge-weidmuller-awpd-35-4x6-6x2-5.png
35mm² to 2.5mm²
Parents
  • MJ, what do you mean by “safe”? Having decided that you can begin to understand what you are asking. Does safe consider the following, and if so why:

    Downstream load characteristics

    Likelihood of a particular fault

    Corresponding fault current

    Catoragise damage from the fault, and consequences

    Lets assume the 35mm comes in from a 200A MCCB, and the outgoing small circuits are bits of control electronics as an example. Fill in the list and then you will see why it may not be necessary to “fuse down” everything. Please reply with your thoughts.

     

     

Reply
  • MJ, what do you mean by “safe”? Having decided that you can begin to understand what you are asking. Does safe consider the following, and if so why:

    Downstream load characteristics

    Likelihood of a particular fault

    Corresponding fault current

    Catoragise damage from the fault, and consequences

    Lets assume the 35mm comes in from a 200A MCCB, and the outgoing small circuits are bits of control electronics as an example. Fill in the list and then you will see why it may not be necessary to “fuse down” everything. Please reply with your thoughts.

     

     