Terminal blocks - no fusing down?

Whenever transitioning from a preceding supply cable protected by a higher current circuit breaker or fuse, I always fuse down before connecting the appropriate lower gauge wire.

 

What I wonder is then how such distribution blocks like these Weidmüller AWPD 35 4X6/6X2.5 are safe:

 

336b015b6f6025bb0464050c14dff2fc-huge-weidmuller-awpd-35-4x6-6x2-5.png
35mm² to 2.5mm²
Parents
  • Precisely, my thinking is that fusing down should protect lower gauge wire feeding other circuits.  In the same way when carrying out a PAT, you would typically replace a plug fuse attached to a figure 8 flex for 5A or 3A.

    Keep in mind that almost all of the rest of the world manages perfectly well with unfused plugs - so there appliance leads are protected by faults only by the MCB or fuse back at the distribution board - typically 15A, 16A or 20A.  Once you understand that protecting conductors from fault currents is quite a different proposition from protecting the same conductor from overload, it all becomes a lot clearer.

        - Andy.

Reply
  • Precisely, my thinking is that fusing down should protect lower gauge wire feeding other circuits.  In the same way when carrying out a PAT, you would typically replace a plug fuse attached to a figure 8 flex for 5A or 3A.

    Keep in mind that almost all of the rest of the world manages perfectly well with unfused plugs - so there appliance leads are protected by faults only by the MCB or fuse back at the distribution board - typically 15A, 16A or 20A.  Once you understand that protecting conductors from fault currents is quite a different proposition from protecting the same conductor from overload, it all becomes a lot clearer.

        - Andy.