This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

EV install on a TT system - DNO PME?

Former Community Member
Former Community Member

Hi, new to this forum.

These might be obvious questions but I can't find an answer to it. 

Background.

A domestic house has a TT supply, has had a CU changed in 2019 but the new owners have no paperwork.

I can find no evidence of an earth rod anywhere and all the bonding cables go to the gas/water supplies. I did a quick Zs at the board = 2.9ohms. 

How do I know if the installation has been PME'd on the pole? (overhead wires)

Second part is - they want an EV charger installed that they brought with them from their old house. It will require TT, but as this property is TT it shouldn't need to have a separate rod.

If the installation is  a PME'd TT I would assume I would need to TT the EV?

Parents
  • Why is that Colin? Is that because they do not appear to be oversleeved with the correct identifying coloured sleeving? Is that S.W.A. at the black Wiska box?

     

    Z.

Reply
  • Why is that Colin? Is that because they do not appear to be oversleeved with the correct identifying coloured sleeving? Is that S.W.A. at the black Wiska box?

     

    Z.

Children
No Data