This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

6mm bonding - new build and Type C RCBOs

Hi, 

I am in the process of buying a new house (new build), and of course checked out the electrical supply. 
 

The gas and water both have what looks like a 6mm bond on a supply clearly marked PME. I would expect that the gas and water are both plastic to the point of entry. 

I have also noticed that the consumer unit has a mixture of type B and type C MCBs. 
 

Kitchen ring = 32A C 

Down sockets 1 = 20A B 

Down sockets 2 = 20A C 

First sockets = 20A B

Down lights = C10 

Up lights = C10 

All RCBOs. 

I know there is nothing inherently wrong with type C in domestic, as long as the ZS is within limits, but I haven’t seen this done before.

Any suggestions or feedback? 

Obviously I haven’t been able to strip the system back and see how it’s been installed, quality etc, but the water/gas bond has thrown me a bit. The vendor said it’s been signed off by a contractor. The install does look very tidy. 
 

Thank you. 

 

Parents
  • I thought you meant the water in the pipes.

Reply
  • I thought you meant the water in the pipes.

Children
No Data