Circuit breakers flashing over or exploding

choosing my words carefully here.

 

Resetting MCBs in a DB or in a machine control panel.  

We have people who are trained in MCB resetting, contactor trips etc inside control panels, and the Schneider MCBs in a dis board are rated for operation by ordinary persons. 

 

I recently lectured someone on the danger of resetting something with the power energised in a control panel, and reminded him that it must be isolated before opening the door (even interlocked isolators can be turned on with the door open. 

 

Well, low and behold, a breaker tripped, panel was isolated correctly, breaker reset, panel turned back on and the MCB and contactor blew up

 

At least it illustrated my point but does this happen much? I have seen it a few times in my years and never in a dis board. Reading the thread about arc flashes has made me think, and if he had his hand on it as it blew up, there would have been an injury of some sort.

 

I'm just thinking about things really, id be interested in your experience of this

Parents
  • Kelly Marie Angel: 
     

    I've only ever known one breaker fail this way. It was a breaker controlling 4 3 phase fan motors  it flashed over when being reset and tripped a 300 amp breaker in the main panel. 

    Possibly due to the inductive loads all working together causing a high Voltage arc.

    Z.

Reply
  • Kelly Marie Angel: 
     

    I've only ever known one breaker fail this way. It was a breaker controlling 4 3 phase fan motors  it flashed over when being reset and tripped a 300 amp breaker in the main panel. 

    Possibly due to the inductive loads all working together causing a high Voltage arc.

    Z.