Equipment in bathroom cupboard

Hi, 

The regs stipulate zones for bathrooms, however I need some guidance on bathroom cupboards.

I have completed an inspection where there is heating control equipment located inside of the bathroom cupboard. This is mounted inside of an IP rated enclosure with a sealed transparent hinged door. There are no metallic parts, no switches etc, just the digital interface for the product itself. 

There is also a network switch, mounted inside of a locked rack enclosure. 
 

Am I right in thinking this is OK and I can treat this as a separate location? 

There are no sockets or switches on show - only 13amp unswitched fused connections. 
 

Thanks. 

Parents
  • Mike, Graham, thank you - I think that I have the picture.

    I can visualize the current through the bath water like the flux around a bar magnet. Most of the resistance of the skin will be lost, so with a conservative figure of 1000 ohms for body resistance, 10% of mains voltage will give a 23 mA shock, which is more than enough.

    I also take the point about drowning, but I would expect the autopsy to differentiate that from VF.

Reply
  • Mike, Graham, thank you - I think that I have the picture.

    I can visualize the current through the bath water like the flux around a bar magnet. Most of the resistance of the skin will be lost, so with a conservative figure of 1000 ohms for body resistance, 10% of mains voltage will give a 23 mA shock, which is more than enough.

    I also take the point about drowning, but I would expect the autopsy to differentiate that from VF.