Shower circuit design.

Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?

Parents
  • Because they had that size cable to hand.

    Because the cable needs de-rating for thermal insulation or grouping.

    To allow for future use of a large shower and larger MCB without the disruption of changing the cable.