Shower circuit design.

Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?

Parents
  • Unless the cable's running through an awful lot of thermal insulation….

Reply
  • Unless the cable's running through an awful lot of thermal insulation….