Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?
Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?
Sparkingchip:
Chris Pearson:
Ignorance?
That is where I’m heading, the 10 mm cable is okay, possibly over the top, but not an issue.
It is the 32 amp circuit breaker I have an issue with.
I agree. Even if the shower is rated 8.5 kW at 240 V, you still have to account for a load of 35.4 A. (If it's 8.5 kW at 230 V, that's 37 A.)
It certainly is unlikely to meet the loading factor criteria for the CU.
Sparkingchip:
Chris Pearson:
Ignorance?
That is where I’m heading, the 10 mm cable is okay, possibly over the top, but not an issue.
It is the 32 amp circuit breaker I have an issue with.
I agree. Even if the shower is rated 8.5 kW at 240 V, you still have to account for a load of 35.4 A. (If it's 8.5 kW at 230 V, that's 37 A.)
It certainly is unlikely to meet the loading factor criteria for the CU.