Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?
Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?
mapj1:
I agree (though I missed it in the original Q too) that anyone claiming the competence to install an 8.5kw shower should be up to division of watts by 230 to get a current
Or 240 … see earlier posts. For example, this 8.5 kW shower is only 8.5 kW at 240 V, 7.8 kW at 230 V (although still if you have a look at page 2 of the manufacturer's instructions, a B40 is recommended by the manufacturer).
mapj1:
I agree (though I missed it in the original Q too) that anyone claiming the competence to install an 8.5kw shower should be up to division of watts by 230 to get a current
Or 240 … see earlier posts. For example, this 8.5 kW shower is only 8.5 kW at 240 V, 7.8 kW at 230 V (although still if you have a look at page 2 of the manufacturer's instructions, a B40 is recommended by the manufacturer).