Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?

Parents
  • Sparkingchip: 
     

    Sparkingchip: 
     

    1d7e13bee47d360d5f1aa4dd780f6d6b-original-20210731_183737.jpg

    Which is the same answer as you get from the Wiring Regulations.

    Sparkingchip, I think you have missed the point that Regulation 411.3.3 only applies where protection against overload is required. It's arguably not required for a shower (although see my earlier post, I would prefer it).

    However, I'd agree it makes not a blind bit of difference if the shower manufacturer is recommending a B40, and also if you take into account frequent overload and loading factors for the CU and adjacent mcb's …I would never select In < Ib.

Reply
  • Sparkingchip: 
     

    Sparkingchip: 
     

    1d7e13bee47d360d5f1aa4dd780f6d6b-original-20210731_183737.jpg

    Which is the same answer as you get from the Wiring Regulations.

    Sparkingchip, I think you have missed the point that Regulation 411.3.3 only applies where protection against overload is required. It's arguably not required for a shower (although see my earlier post, I would prefer it).

    However, I'd agree it makes not a blind bit of difference if the shower manufacturer is recommending a B40, and also if you take into account frequent overload and loading factors for the CU and adjacent mcb's …I would never select In < Ib.