Shower circuit design.

Why would an electrician install a 10 mm twin and earth circuit protected by a B32 MCB for a 8.5 kW shower?

Parents
  • Surely the breaker is protecting the cable, not the load. By that logic it should have a 37A breaker then to protect the shower? If the cable is big enough to take 45A then it could have a 5w LED lamp on the end and still be ok

Reply
  • Surely the breaker is protecting the cable, not the load. By that logic it should have a 37A breaker then to protect the shower? If the cable is big enough to take 45A then it could have a 5w LED lamp on the end and still be ok