Interaction between Ventilation fan and LED light

I was asked to investigate an issue, an extractor fan had been installed in the loft above a bathroom, connected to an LED light fitting in the bathroom. When the light is turned on the fan runs, when the light is turned off the fan ‘pulses’ and the light ‘strobes’. ie both are on for ~1 sec then off for several seconds repeatedly. There are two bathrooms (family and en-suite) with identical fans but different LED light fittings. Both fans work correctly with the en-suite light, both fans exhibit the same problem with the main bathroom light. I believe that my tests have also excluded any local wiring faults 

I have raised the issue with the fan manufacturers and they say they have only seen this once before and was cured by fitting a ballast resistor (presumably in the light). I don't really want to do this as it negates the energy saving of the LED (and will generate unwanted heat). I suspect some strange interaction between the LED driver circuit and the fan timer circuit, either due to power factor or resonance (the light flash is similar to a faulty fluorescent light), in which case a coil or capacitor might be more appropriate.

Has any one else seen this? If so what did you do to solve it?

 

Parents
  • SOLVED I went through the wiring from end to end and discovered that the incoming neutral had a brown sleeve indicating it was switched live. Hence light has been running with sw live and neutral transposed which only became apparent recently when the fan was instaĺled.. Worrying, as the lights were installed by a ‘qualified electrician’ as part of an EICR who insisted that new lights were required ‘to comply with the new regs’.

Reply
  • SOLVED I went through the wiring from end to end and discovered that the incoming neutral had a brown sleeve indicating it was switched live. Hence light has been running with sw live and neutral transposed which only became apparent recently when the fan was instaĺled.. Worrying, as the lights were installed by a ‘qualified electrician’ as part of an EICR who insisted that new lights were required ‘to comply with the new regs’.