Are Single cores outside enclosure classed as a C2 for a EICR? 

thanks for your answers in advance

Parents
  • Chris Pearson: 
     

    MrJack96: 
     

    8e1b3af4fc7544d13743723b47d03238-huge-020b610a-a595-45a0-a34b-cdb4e6b2b93a.jpg


    C2? 

    Yes, but let's think about it.

    What is the gland made of? It does not look like brass. If the sheath is the CPC, it has been lost so that's C2 plain and simple.

    The risk of conductors becoming detached is high. If that is on the load side of the box, and everything came out, no problem; but if one of them is the CPC, that's back to C2. If the conductors are TPN, the consequences of one becoming detached depends upon what is at the other end.

    There doesn't look to be a protective conductor connected to the gland, although that in itself may or may not be an issue - it might be earthed at the other end.

    Is it a mains cable or a control cable operating PELV (although the latter would still require an earthed armour if the cable is buried).

Reply
  • Chris Pearson: 
     

    MrJack96: 
     

    8e1b3af4fc7544d13743723b47d03238-huge-020b610a-a595-45a0-a34b-cdb4e6b2b93a.jpg


    C2? 

    Yes, but let's think about it.

    What is the gland made of? It does not look like brass. If the sheath is the CPC, it has been lost so that's C2 plain and simple.

    The risk of conductors becoming detached is high. If that is on the load side of the box, and everything came out, no problem; but if one of them is the CPC, that's back to C2. If the conductors are TPN, the consequences of one becoming detached depends upon what is at the other end.

    There doesn't look to be a protective conductor connected to the gland, although that in itself may or may not be an issue - it might be earthed at the other end.

    Is it a mains cable or a control cable operating PELV (although the latter would still require an earthed armour if the cable is buried).