Single cores outside enclosure

Are Single cores outside enclosure classed as a C2 for a EICR? 

thanks for your answers in advance

Parents
  • AJJewsbury: 
     

    gkenyon: 
     

    AJJewsbury: 
    Non-compliance, but not necessarily a C2. Say we had non-sheathed cables on a SELV circuit (e.g. traditional bell wire on a door bell circuit) - is that really even a codable situation?

       - Andy.

    But this is LV ?

    The point I was attempting to make was that there's nothing in the wording or positioning of 521.10.1 to say it only applies to LV circuits… using exposed non-sheathed cables in other situations would thus still be a non-compliance, but the danger would likely not be significant.

       - Andy.

    Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all … give or take any additional requirements where a Part 7 applies of course.

Reply
  • AJJewsbury: 
     

    gkenyon: 
     

    AJJewsbury: 
    Non-compliance, but not necessarily a C2. Say we had non-sheathed cables on a SELV circuit (e.g. traditional bell wire on a door bell circuit) - is that really even a codable situation?

       - Andy.

    But this is LV ?

    The point I was attempting to make was that there's nothing in the wording or positioning of 521.10.1 to say it only applies to LV circuits… using exposed non-sheathed cables in other situations would thus still be a non-compliance, but the danger would likely not be significant.

       - Andy.

    Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all … give or take any additional requirements where a Part 7 applies of course.