Are Single cores outside enclosure classed as a C2 for a EICR?
thanks for your answers in advance
Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all …
Basic insulation might be omittable for safety reasons (even if it's almost certainly still needed for functional reasons) - but the words of 521.10.1 still seem to require a sheath (or conduit, ducting or trunking) regardless. Even bare conductors would be unsheathed.
- Andy.
Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all …
Basic insulation might be omittable for safety reasons (even if it's almost certainly still needed for functional reasons) - but the words of 521.10.1 still seem to require a sheath (or conduit, ducting or trunking) regardless. Even bare conductors would be unsheathed.
- Andy.