Single cores outside enclosure

Are Single cores outside enclosure classed as a C2 for a EICR? 

thanks for your answers in advance

Parents
  • AJJewsbury: 
     

    Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all … 

    Basic insulation might be omittable for safety reasons (even if it's almost certainly still needed for functional reasons) - but the words of 521.10.1 still seem to require a sheath (or conduit, ducting or trunking) regardless. Even bare conductors would be unsheathed.

       - Andy.

     

     

    Bare conductors may be installed on insulators … Regulation 521.10.201

    I do agree, though … and for fire safety as I've said it may well be necessary even for ELV systems (perhaps more so than LV systems, particularly if the current available is above a few amperes. It's perhaps less likely to be immediately dangerous if ELV … 

     

Reply
  • AJJewsbury: 
     

    Does Regulation 414.4.5 not apply in the general case where the voltage is less than 25 V AC or 60 V DC … no basic protection (including insulation) is necessary at all … 

    Basic insulation might be omittable for safety reasons (even if it's almost certainly still needed for functional reasons) - but the words of 521.10.1 still seem to require a sheath (or conduit, ducting or trunking) regardless. Even bare conductors would be unsheathed.

       - Andy.

     

     

    Bare conductors may be installed on insulators … Regulation 521.10.201

    I do agree, though … and for fire safety as I've said it may well be necessary even for ELV systems (perhaps more so than LV systems, particularly if the current available is above a few amperes. It's perhaps less likely to be immediately dangerous if ELV … 

     