Are Single cores outside enclosure classed as a C2 for a EICR?
thanks for your answers in advance
Bare conductors may be installed on insulators … Regulation 521.10.201
Indeed, but as written there's nothing to say 521.10.1 doesn't simultaneously apply - as the bare conductors are unsheathed they (and presumably the insulators) would have to be within trunking (or ducting or conduit).
- Andy.
Bare conductors may be installed on insulators … Regulation 521.10.201
Indeed, but as written there's nothing to say 521.10.1 doesn't simultaneously apply - as the bare conductors are unsheathed they (and presumably the insulators) would have to be within trunking (or ducting or conduit).
- Andy.