Battery backup earthing - PME supply

Hi, 

I am installing a battery (Alpha ESS) to a PME system. 

The battery charges during off-peak and discharges during the day during peak hours. There is no solar. 

This relatively straight forward and will be notified to the DNO. 

The system features a back-up supply, where if the grid supply fails, a set of loads can be powered from a dedicated “backup” output on the inverter. This output is already separate from the grid input. 

The question I have is around earthing. When in normal operation the inverter is connected to the PME supply via the MET in the distribution board and the “backup” output is earthed through this connection. When the grid fails (outage, for example) my thinking is that the PME “earth” cannot be relied upon for the backup circuit (lost neutral for example). 

What would be the best course of action to resolve this situation? 

  1. Earth rod at the customer premises connected to the MET? 
  2. Rely on the manual and it’s wiring diagram? 
  3. Other? 
     

The inverter manual gives no indication. 

Thanks.

Battery Inverter Manual: 

https://www.alpha-ess.com/Upload/Images/20190814093353_165226.pdf

Parents
  • There is no problem having the DNO's earthing terminal connected to MET at the same time as your own earth electrode (just like extraneous-conductive-parts). In fact, a consumer's supplementary earth electrode is recognized by BS 7671. See Fig 3.9 and the descriptions below it.

    What you MUST NOT do is connect N to PE within your installation (downstream of the DNO's service head), without disconnecting the distributor's neutral first - regardless of whether the supply is TN-C-S (PME), TN-S, or TT. This is not only an issue for protective devices, but also potentially contravenes ESQCR.

    It's absolutely fine for the appropriate switching devices (island mode isolator to disconnect the distributor's live conductors, all lines and Neutral and the N-E bond relay to form TN-S when the grid is fully disconnected) to be part of the inverter, battery management system, etc., provided they meet these requirements.

    You will, of course, need to provide the additional consumer earth electrode if one is not already present. The value of electrode resistance required will depend on the size of RCD used for the island-mode circuits ("essential loads") and whether there are any other complications such as TT-d outbuildings or EV charging points.

    You must ensure that protection against electric shock and overcurrent are available in all modes of operation.

    Because an EESS charges the battery as well as as discharging it, you will need to check the rating of the CU is not exceeded. For example, if the CU is rated for 100 A, and there's a 100 A service fuse, and a 16 A output battery storage system - by feeding 16 A in at one end through an OCPD, because that OCPD gets hot it contributes to the total heat load in the CU - therefore the CU should be rated for 116 A.

    All of this is covered in the IET Code of Practice for Electrical Energy Storage Systems.

Reply
  • There is no problem having the DNO's earthing terminal connected to MET at the same time as your own earth electrode (just like extraneous-conductive-parts). In fact, a consumer's supplementary earth electrode is recognized by BS 7671. See Fig 3.9 and the descriptions below it.

    What you MUST NOT do is connect N to PE within your installation (downstream of the DNO's service head), without disconnecting the distributor's neutral first - regardless of whether the supply is TN-C-S (PME), TN-S, or TT. This is not only an issue for protective devices, but also potentially contravenes ESQCR.

    It's absolutely fine for the appropriate switching devices (island mode isolator to disconnect the distributor's live conductors, all lines and Neutral and the N-E bond relay to form TN-S when the grid is fully disconnected) to be part of the inverter, battery management system, etc., provided they meet these requirements.

    You will, of course, need to provide the additional consumer earth electrode if one is not already present. The value of electrode resistance required will depend on the size of RCD used for the island-mode circuits ("essential loads") and whether there are any other complications such as TT-d outbuildings or EV charging points.

    You must ensure that protection against electric shock and overcurrent are available in all modes of operation.

    Because an EESS charges the battery as well as as discharging it, you will need to check the rating of the CU is not exceeded. For example, if the CU is rated for 100 A, and there's a 100 A service fuse, and a 16 A output battery storage system - by feeding 16 A in at one end through an OCPD, because that OCPD gets hot it contributes to the total heat load in the CU - therefore the CU should be rated for 116 A.

    All of this is covered in the IET Code of Practice for Electrical Energy Storage Systems.