Garage supply

Former Community Member
Former Community Member

Hi all,

 

I’ve recently been asked for advice and found myself reluctant to give an answer without a second opinion.

Question - 

Is it possible to run in a garage supply using 4mm SWA off the house ring and protect the garage via a CU - 25A RCD with 16A and 6A MCB for sockets and lighting? 

The garage is located at the very back of the house, the DB is at the very front and there is one ring circuit for the upstairs and downstairs (Kitchen is on its own ring).

My personal opinion would be to run in a new supply from the board in the house, however accessibility is supposedly an issue and the house has been recently renovated. For which reason this method of supply has been suggested. 
 

Many thanks in advance,

 

Jack 

Parents
  • AJJewsbury: 
     

    If the circuit supplies a CU, then it's no longer a ring final circuit by definition.

    I don't read the definitions that way - not unless the ring supplies just the CU and no sockets at all. A ring connected to both sockets and a CU is still ‘directly connected to a socket outlet or socket outlets’ so meets the definition for a final circuit … and sensibly still has to meet final circuit requirements (0.4s disconnection time etc). (Same as if a ring supplied a mix of FCUs and sockets). The choice of the word ‘final’ is perhaps a bit unfortunate given its usual menaing in English, but the definitons don't seem encumbered by that.

       - Andy.

    This is really tricky. If the garage were a separate building in the premises, see definition of distribution circuit … where the distinction would be far clearer.

    The important points in a case like this are:

    • the circuit is no longer one of the considered standard final circuit arrangements. I agree that if loads in the garage are typically inconsequential, that's no different to a couple of spurs in a single location. However, if loads might be significant (a couple of potentially heavy-current using appliances in there like tumble dryer and washing machine), it may upset the current balance of the ring.
    • we have reduced selectivity that two separate circuits would provide - faults in the garage disconnect the ring final circuit and vice-versa - including a fault in an appliance in the house taking out the light in the garage, which may (or equally may not) be a safety issue.
    • the definition for final circuit in BS 7671 doesn't always fit the real world.
Reply
  • AJJewsbury: 
     

    If the circuit supplies a CU, then it's no longer a ring final circuit by definition.

    I don't read the definitions that way - not unless the ring supplies just the CU and no sockets at all. A ring connected to both sockets and a CU is still ‘directly connected to a socket outlet or socket outlets’ so meets the definition for a final circuit … and sensibly still has to meet final circuit requirements (0.4s disconnection time etc). (Same as if a ring supplied a mix of FCUs and sockets). The choice of the word ‘final’ is perhaps a bit unfortunate given its usual menaing in English, but the definitons don't seem encumbered by that.

       - Andy.

    This is really tricky. If the garage were a separate building in the premises, see definition of distribution circuit … where the distinction would be far clearer.

    The important points in a case like this are:

    • the circuit is no longer one of the considered standard final circuit arrangements. I agree that if loads in the garage are typically inconsequential, that's no different to a couple of spurs in a single location. However, if loads might be significant (a couple of potentially heavy-current using appliances in there like tumble dryer and washing machine), it may upset the current balance of the ring.
    • we have reduced selectivity that two separate circuits would provide - faults in the garage disconnect the ring final circuit and vice-versa - including a fault in an appliance in the house taking out the light in the garage, which may (or equally may not) be a safety issue.
    • the definition for final circuit in BS 7671 doesn't always fit the real world.