Hi all,

 

I’ve recently been asked for advice and found myself reluctant to give an answer without a second opinion.

Question - 

Is it possible to run in a garage supply using 4mm SWA off the house ring and protect the garage via a CU - 25A RCD with 16A and 6A MCB for sockets and lighting? 

The garage is located at the very back of the house, the DB is at the very front and there is one ring circuit for the upstairs and downstairs (Kitchen is on its own ring).

My personal opinion would be to run in a new supply from the board in the house, however accessibility is supposedly an issue and the house has been recently renovated. For which reason this method of supply has been suggested. 
 

Many thanks in advance,

 

Jack 

  • If the circuit supplies a CU, then it's no longer a ring final circuit by definition.

    I don't read the definitions that way - not unless the ring supplies just the CU and no sockets at all. A ring connected to both sockets and a CU is still ‘directly connected to a socket outlet or socket outlets’ so meets the definition for a final circuit … and sensibly still has to meet final circuit requirements (0.4s disconnection time etc). (Same as if a ring supplied a mix of FCUs and sockets). The choice of the word ‘final’ is perhaps a bit unfortunate given its usual menaing in English, but the definitons don't seem encumbered by that.

       - Andy.

  • My take is that a ring final cct is a final cct in its own right. However if a further fuseway (fuse or breaker for example ) is attached then the downstream circuit is also a cct in its own right and the ring final supplying it is its distribution cct.

    So, a ring final circuit is a final circuit and if supplies another (fixed) circuit is is also a distribution circuit.

    Some tings are one category some are another and some are both. 

    Of course a plugtop plugged into a socket on that ring running say a kettle, lets it run the kettle and is its own circuit but it is not part of the fixed installation.

  • Well indeed - is a 4 way block extension lead screwed to the wall above the worktop a ‘final sub-circuit’ ? Perhaps by some definition, but you'd still consider the sockets on the ring it plugs into to be part of a final circuit too, not just distribution. I'd strongly suggest not worrying too much about it.

    Rather like a biologist wondering which of the entirely man made categories the platypus belongs in - the platypus is not affected and does not care.

    Mike.

  • AJJewsbury: 
     

    If the circuit supplies a CU, then it's no longer a ring final circuit by definition.

    I don't read the definitions that way - not unless the ring supplies just the CU and no sockets at all. A ring connected to both sockets and a CU is still ‘directly connected to a socket outlet or socket outlets’ so meets the definition for a final circuit … and sensibly still has to meet final circuit requirements (0.4s disconnection time etc). (Same as if a ring supplied a mix of FCUs and sockets). The choice of the word ‘final’ is perhaps a bit unfortunate given its usual menaing in English, but the definitons don't seem encumbered by that.

       - Andy.

    This is really tricky. If the garage were a separate building in the premises, see definition of distribution circuit … where the distinction would be far clearer.

    The important points in a case like this are:

    • the circuit is no longer one of the considered standard final circuit arrangements. I agree that if loads in the garage are typically inconsequential, that's no different to a couple of spurs in a single location. However, if loads might be significant (a couple of potentially heavy-current using appliances in there like tumble dryer and washing machine), it may upset the current balance of the ring.
    • we have reduced selectivity that two separate circuits would provide - faults in the garage disconnect the ring final circuit and vice-versa - including a fault in an appliance in the house taking out the light in the garage, which may (or equally may not) be a safety issue.
    • the definition for final circuit in BS 7671 doesn't always fit the real world.
  • This is really tricky. If the garage were a separate building in the premises, see definition of distribution circuit … where the distinction would be far clearer.

    I agree with ebee, I think it only seems tricky if you assume that a circuit can't be both a distribution circuit and a final circuit at the same time. If you accept that it can, things seem to slot into place.

    In some situations - e.g. temporary event setups - having a DB supplied from a plug & socket would be perfectly normal. Our ring final also supplying a garage CU (or a whole stack of FCUs) is no different in principle. BS 7671 should be able to cope - and the definitions seem to (there's nothing in the definition of a distribution circuit to say it's not a final circuit, or vice versa).

    The wording of 411.3.2.3 and 411.3.2.4 might need another look though…

       - Andy.

  • In one way, that's where I'm going … if one were to decide that a circuit could be both a final circuit and a distribution circuit, then you agree it's not purely a final circuit … which then means it could well be a “circuit not covered by Regulation 411.3.2.2”.

    It may also mean that where other regulations concern final circuits, they too could also be either used or ignored at will …