The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Immersion Heater Wiring.

A customer has an economy 7 immersion heater to heat water in a copper cylinder. That is all she has to heat the water, one element.

She needs a boost function. Easy I thought. Just install a boost timer control.

But the existing immersion heater is supplied from a non R.C.D. protected off peak board. The booster switch will need to be fed from a 24 hour on peak board. All the on peak boards are R.C.D. protected via one R.C.D.

 

So, what is the easiest way to switch from off peak to on peak boost whilst not getting the neutrals interconnected, and with an automatic default back to off peak after the boost period?

 

I was thinking about a double pole changeover contactor. Is there another way?

 

Z.

Parents
  • Sparkymark: 
     

    How about changing the element for a dual element?

    The copper cylinder is very distant from the consumer unit and only has an off peak supply cable.

     

    Z.

Reply
  • Sparkymark: 
     

    How about changing the element for a dual element?

    The copper cylinder is very distant from the consumer unit and only has an off peak supply cable.

     

    Z.

Children
No Data