A customer has an economy 7 immersion heater to heat water in a copper cylinder. That is all she has to heat the water, one element.

She needs a boost function. Easy I thought. Just install a boost timer control.

But the existing immersion heater is supplied from a non R.C.D. protected off peak board. The booster switch will need to be fed from a 24 hour on peak board. All the on peak boards are R.C.D. protected via one R.C.D.

 

So, what is the easiest way to switch from off peak to on peak boost whilst not getting the neutrals interconnected, and with an automatic default back to off peak after the boost period?

 

I was thinking about a double pole changeover contactor. Is there another way?

 

Z.

Parents
  • Sparkingchip: 
     

    There’s only one way of doing it, E7 controller from the peak supply.

    Anything else is too involved.

    Are the simple economy 7 immersion heater controllers with a boost facility and simple 24 hour rotary time switch still made?

     

    Z.

Reply
  • Sparkingchip: 
     

    There’s only one way of doing it, E7 controller from the peak supply.

    Anything else is too involved.

    Are the simple economy 7 immersion heater controllers with a boost facility and simple 24 hour rotary time switch still made?

     

    Z.