This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Main and sub distribution boards - Circuit Breakers

a. I have a UPS (200kVA) at 230V 3 phase output, the ampere rating is 500A which feeds the main distribution board.
b. The Main Distribution Board has an Incoming MCCB with 630A and there are several outgoing circuit breakers at the Main distribution board, out of which 1 circuit breaker is of 25A MCB (Q1) 3P powers the secondary distribution board. 

c. The cable between the the Main distribution board and the secondary distribution board is protected against overloads and short-circuits by the mentioned circuit breaker (Q1)

d. At the arrival of the Secondary Distribution Board I have a 25A 4P Switch Disconnector (S1)

e. There are several outgoing circuit breakers at the secondary distribution board, out of which one  circuit breaker is of 25A MCB (Q2) 3P

1. How do I check manually that circuit breaker (Q1) is discriminated against the fault at the secondary of the outgoing breakers at the secondary distribution board?
2. Should I install 6A or 10A MCB in place of 25A MCB (Q2) to have a better discrimination
3. Do any standard limit the number of circuit breakers in the secondary distribution board? If no standard states it, what is the general engineering practice?

4. Should I have 4P MCB in place of 3P 25A MCB (Q1). When do I need to have 4P MCB?

Parents
  • Say, if I want to increase the downstream breaker rating, for discrimination purposes I should increase the rating of the Upstream breaker in which case for a fault current at the feeder, the upstream breaker (if it is type C) may not act in time and the cable becomes fuse. I wanted to avoid this

Reply
  • Say, if I want to increase the downstream breaker rating, for discrimination purposes I should increase the rating of the Upstream breaker in which case for a fault current at the feeder, the upstream breaker (if it is type C) may not act in time and the cable becomes fuse. I wanted to avoid this

Children
No Data