Supply to feeder pillar - no incomer?

Hello lovely folks, I have a question about arrangement I came across which I am not familiar with and wanted to pick your brains up on the matter.

I have a new packaged substation that is being put in on our site which has a 11kV/0.4kV transformer with busbars on LV side connecting into the LV Feeder pillar where then you tap off directly with submains to MCCBs feeding subcircuits around site. Now what I usually saw was one supply to a feeder pillar with incomer protection in form of a fused switch or ACB and then distributing around smaller MCCBs. 

In this instance there is no isolating switch, just busbars going to smaller MCCBs and G99 relay for transformer protection within the feeder pillar. What do you guys think about this arrangement, pros and cons? It just feels odd to me not having any isolating switch on the main incomer.

 

Parents
  • First thought: Not my preferred arrangement, and I've seen this kind of thing end badly.

    Sounds like a solar park to me, or similar… What does the G99 relay operate - a main contactor somewhere or each of the generators? Where (and what) are the main and emergency points of isolation (maybe at HV)?

    The HV designer should be able to provide comfort that the transfomer feeder protection provides cover for LV faults within sufficient time at least as far as the MCCBs (including earth faults)… Being close-coupled in principle the answer should be similar to having an upfront ACB, but the risk of internal faults is somewhat increased (particularly given the application). Note that even if it does it is likely to be significantly slower than an LV protective device so resulting damage will be considerably greater.

    Conversely the MCCBs (and any auxiliary circuit OCPDs) would need to be rated for the full prospective fault of the transformer, since there's no backup/current limiting. so they might be bigger than you'd otherwise need.

    Is overload protection needed?

    Is it satisfactory that HV operations are required to maintain and inspect the LV switchboard The construction / separation / form of the switchboard will also inform the discussion.

Reply
  • First thought: Not my preferred arrangement, and I've seen this kind of thing end badly.

    Sounds like a solar park to me, or similar… What does the G99 relay operate - a main contactor somewhere or each of the generators? Where (and what) are the main and emergency points of isolation (maybe at HV)?

    The HV designer should be able to provide comfort that the transfomer feeder protection provides cover for LV faults within sufficient time at least as far as the MCCBs (including earth faults)… Being close-coupled in principle the answer should be similar to having an upfront ACB, but the risk of internal faults is somewhat increased (particularly given the application). Note that even if it does it is likely to be significantly slower than an LV protective device so resulting damage will be considerably greater.

    Conversely the MCCBs (and any auxiliary circuit OCPDs) would need to be rated for the full prospective fault of the transformer, since there's no backup/current limiting. so they might be bigger than you'd otherwise need.

    Is overload protection needed?

    Is it satisfactory that HV operations are required to maintain and inspect the LV switchboard The construction / separation / form of the switchboard will also inform the discussion.