Type B rcd availability

Hi

would anyone know of a supplier where I could get my hands on a 100A 100ma type B double pole rcd? I need one to supply three variable speed inverters. I’ve done the usual google searches but can only find 30ma ones and only rated up to 63A. 
 

Thanks in advance

Parents
  • could you consider  

    a slow trip (s-type) first to ride the inrush, if that is what it is causing the trips. 

    Or filters if it is an HF / spikes issue. 

    Or filters wired a kind of ‘open delta’ if earth “leakage ” from RFI filters is the issue. (so we put filter caps L-L-L and L-N,  but not large ones L-E. We then have a larger one NE)  Can sometimes be done after the fact by ‘neutralling’  the earth terminal of a traditional potted filter, putting it in a plastic box and taking the CPC around it.

    Mike.

     

Reply
  • could you consider  

    a slow trip (s-type) first to ride the inrush, if that is what it is causing the trips. 

    Or filters if it is an HF / spikes issue. 

    Or filters wired a kind of ‘open delta’ if earth “leakage ” from RFI filters is the issue. (so we put filter caps L-L-L and L-N,  but not large ones L-E. We then have a larger one NE)  Can sometimes be done after the fact by ‘neutralling’  the earth terminal of a traditional potted filter, putting it in a plastic box and taking the CPC around it.