Hi

would anyone know of a supplier where I could get my hands on a 100A 100ma type B double pole rcd? I need one to supply three variable speed inverters. I’ve done the usual google searches but can only find 30ma ones and only rated up to 63A. 
 

Thanks in advance

Parents
  • Another point, my lathe VSD (single-phase in 3 phase out, 4kW) does not trip a type AC ever, neither does the 3kW SP motor on my compressor on 99% of the switch on's. It does on the odd occasion which is a B nuisance, but I am not particularly inconvenienced so not worth a soft starter.

    Note that the inverter is wired to start with no load, and then the motor is started with a normal control signal to the inverter which slowly accelerates the motor. It should not be used any other way, although it can act in a soft start manner on power up with some other settings.

Reply
  • Another point, my lathe VSD (single-phase in 3 phase out, 4kW) does not trip a type AC ever, neither does the 3kW SP motor on my compressor on 99% of the switch on's. It does on the odd occasion which is a B nuisance, but I am not particularly inconvenienced so not worth a soft starter.

    Note that the inverter is wired to start with no load, and then the motor is started with a normal control signal to the inverter which slowly accelerates the motor. It should not be used any other way, although it can act in a soft start manner on power up with some other settings.