This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

T-N-S or TN-C-S ???? Help pls.

I have been asked to replace a consumer unit. All seems fine, and the incoming earth seems to be on the sheath of the incomer, so, TN-S. But, it says TN-C-S on the previous EICR. Did that spark make a mistake or is there something here I'm missing? Also, do we presume the Line and Neutral are in that cable going to the meter??? I hope so… Thx in advance.

b13f6e8ca4a8740403be79c8a45433ce-huge-tns_or_tncs.png
Parents
  • Another possible clue is if the neutral earth voltage is only a few hundred millivolt  then chances are that earth and neutral are joined at atleast  a few joints 

     

     

     

     

Reply
  • Another possible clue is if the neutral earth voltage is only a few hundred millivolt  then chances are that earth and neutral are joined at atleast  a few joints 

     

     

     

     

Children
No Data