Why is the Switch disconnector 2 pole device's operational voltage rating at 415V?

Shouldn't the voltage between line and neutral be around 230V in single phase installation?

For example this SD 

Thanks.

 

J

Parents
  • Yes, the single phase L-N voltage in the Uk is 230V

     

    However, why assume this device can only be connected L/N. You might want to connect it to two phases of a 400V system 

Reply
  • Yes, the single phase L-N voltage in the Uk is 230V

     

    However, why assume this device can only be connected L/N. You might want to connect it to two phases of a 400V system 