Is earth rod impedance acceptable

Hi I am trying to work out if I can pass and earth rod loop impedance measurement of 550 ohs, sorry this may be a bit of  a long question.

My customer has a property with a large garage, two detached house and various out buildings all owned by himself. It's a remote location with overhead wires, TT earth and private pumped water supply.

Power comes in to the garage with separate supplies for the two houses. My interest is in the main house, the feed for this supplies the house, garage and various outbuildings. There is a earth rod near the incoming connection in the garage and another rod near the actual house and as you would expect bonding to water pipes.

Using a normal earth loop impedance test yesterday the earth rod near the garage gave me 560 ohms, my understanding is that to be reliable the result should be less than 200 ohms. But on the positive side my Zs @DB with the rest if the earthing connected was 75 ohms. I haven't checked so far but my assumption is that most of this is coming from the private water pipes.

Also this is probably the driest point in the year and earth rod impedance is likely to go down rather than up.

My initial thought was that I need to put another earth rod in but then started thinking that as the water pipes are private it's acceptable to use them for earthing and also is it ok to rely on multiple dispersed earth rods even if they are at the other end of some armoured cables.

As some additional information all the circuits are protected by RCD's. Some by 100mA type S RCD's at the origin and where I have changed the CU i have installed 30mA RCBO's for each circuit. I have installed type 1,2,3 SPD's at the origin and type 2 spd's in the two houses.

Welcome your thoughts on weather I need to install an additional earth rod.

Also if earth rods are protecting two properties on different supplies is it permissible to connect them together. I am asking this because the two rods are about 6 inches apart and the other one is giving a much better result, or would connecting them cause confusion and risk?

Thanks

 

Alan

Parents
  • Hi All

    Thanks for your time.e and answers

    Answering some of the questions

    I inspected connection to top of the rod and it looked OK. Impedance from top of rod to the met was under one ohm.

    To be honest I don't know much about the water pipes once they leave the houses but will investigate further.

    It could be that most of my earth connections are coming from rods. 

    It sounds like I can connect the earth rods from both properties together which would give a significant improvement. I may get a written confirmation of this fro. Napit.

    I think I will also try getting another rod I as its going to be quicker than fault finding. My tester can do various earth rod tests but I don't have the test probes and not sure how often I would use them.

Reply
  • Hi All

    Thanks for your time.e and answers

    Answering some of the questions

    I inspected connection to top of the rod and it looked OK. Impedance from top of rod to the met was under one ohm.

    To be honest I don't know much about the water pipes once they leave the houses but will investigate further.

    It could be that most of my earth connections are coming from rods. 

    It sounds like I can connect the earth rods from both properties together which would give a significant improvement. I may get a written confirmation of this fro. Napit.

    I think I will also try getting another rod I as its going to be quicker than fault finding. My tester can do various earth rod tests but I don't have the test probes and not sure how often I would use them.