EICR Certificate - Should Bathroom light not having RCD protection be C2 or C3?

Hello,

Is anyone able to please clarify?  An electrician has just undertaken an inspection to allow an EICR to be issued.  They have stated there is a requirement to have RCD protection for the bathroom light (given it a code C2) and so they are quoting £600 to fit a new consumer unit.  I appreciate that if the house was being built today that it would need to comply with the 18th edition regs which came into force in Jan 2019 and hence would indeed need an RCD on the bathroom light but my house was built in 1956 although has a 16th edition CU with RCDs on socket circuits only but I thought this should be coded as a C3.  Any advice greatly appreciated.

Thanks

Parents
  • AdamG: 
    If it’s more than 0.05 Ohm then I guess I’ll just bite the bullet and get the electrician to fit a new CU which will have 9 RCBOs for all the existing circuits and SPD …

    Or fit supplementary bonding if the pipes are copper.

Reply
  • AdamG: 
    If it’s more than 0.05 Ohm then I guess I’ll just bite the bullet and get the electrician to fit a new CU which will have 9 RCBOs for all the existing circuits and SPD …

    Or fit supplementary bonding if the pipes are copper.