Diversity and the resilience of circuit protection.

Following a report from a well respected Contributor here, I've been tasked with sorting out a few problems in a house.

One of them is a good lesson in diversity for cooking appliances.

A 45 amp circuit breaker, 6mm T+E cable, running in some patches of insulation, so a nominal 34 amps current carrying capacity. Probably a little more, as the insulation is not continuous, and is patchy in the void the cable runs through.

This cable supplies 6 appliances. Oven 3.6kW, hob 6.2kW,frying plate 2.4kW, large microwave 2.6kW, Steamer 5.6kW and a warming drawer at 0.7kW. A total nominal rating of 94kW.

With the current diversity guidance in the OSG, this install complies (forgetting about the overloaded cable) with the hob at 10 amps, and the rest at 30% of their rating, giving a total of 32 amps but it just doesn't feel right. To get a little better control, and fault reduction, I had intended to put 2 extra new supplies in, to divide them up, I've since put one supply in, but the second one is getting rather difficult to install without taking apart the kitchen.

The oven (16amp) was on a plugtop, with no signs of overheating, or reports of problems from the householder. A 20 amp DP switch, which supplied the steamer, microwave and drawer did show a little heat damage, though that could well have been a loose connection.

So it goes back to the pragmatic view, how much can a small family cook at the same time, and there we have the diversity. They say there are 2 hob rings they never use, the fryer is rarely used etc. So the typical load is less than 3kW once the oven has warmed up.

Even with the Christmas day dinner cooking, I cannot see much more than 30 amps being pulled for a short period, hence no overheating of the cable, and no tripping of the circuit.

The circuit breakers are now 32 amps.

I heard a whisper that guidance on Diversity is changing, has anyone else heard what may be changing? 

Parents
  • Diversity is reliant on a certain amount of estimating and engineering judgement, but the installation as described does sound a bit much on a single 32 amp circuit.

    Probably fine most of the time, but still a bit much if cooking an unusually large meal.

    The standard diversity is primarily intended for a single cooker that incorporates several boiling rings, a grill and at least one oven. It has a good record in practice.

    The standard diversity allowance could reasonably be applied to several appliances that in total are similar in design and application to a standard cooker. For example, two twin boiling rings, an oven and a table top grill, all fitted with 13 amp plugs could in my view be supplied from the same 32 amp circuit despite  the total loading being in excess of 32.

    It is however IMHO debatable if other cooking appliances that would not normally be part of a  standard cooker should be considered in the same way.

    I would normally expect a microwave oven to be plugged in to a 13 amp socket independent of the cooker circuit. And the steamer to have its own circuit, NOT shared with the cooker, or other appliances that approximate in function to a cooker.

     How big is the rest of the house ? this is IMHO indirectly relevant since it partly determines the chances of preparing an elaborate meal for a dozen guests. Or even for a large family.

Reply
  • Diversity is reliant on a certain amount of estimating and engineering judgement, but the installation as described does sound a bit much on a single 32 amp circuit.

    Probably fine most of the time, but still a bit much if cooking an unusually large meal.

    The standard diversity is primarily intended for a single cooker that incorporates several boiling rings, a grill and at least one oven. It has a good record in practice.

    The standard diversity allowance could reasonably be applied to several appliances that in total are similar in design and application to a standard cooker. For example, two twin boiling rings, an oven and a table top grill, all fitted with 13 amp plugs could in my view be supplied from the same 32 amp circuit despite  the total loading being in excess of 32.

    It is however IMHO debatable if other cooking appliances that would not normally be part of a  standard cooker should be considered in the same way.

    I would normally expect a microwave oven to be plugged in to a 13 amp socket independent of the cooker circuit. And the steamer to have its own circuit, NOT shared with the cooker, or other appliances that approximate in function to a cooker.

     How big is the rest of the house ? this is IMHO indirectly relevant since it partly determines the chances of preparing an elaborate meal for a dozen guests. Or even for a large family.