EICR Valid?

Former Community Member
Former Community Member

Hello,

I recieved an EICR for my Private Rented property from the landord. However, the post code of the address is wrong. Is the EICR still valid? It was done over a year ago, so Is it allowed to be corrected via just changing the post code or do the whole electrics need to be retested/inspected?

Parents
  • Day567: 
    I have attached an image of the back page of the EICR document as well as the file for the whole EICR: just to confirm you are saying that due to this being completely blank the EICR is void?

    It isn't so much void as incomplete.

    The paperwork seems to be a bit of a mongrel - it is not the current model form or the one before it. As Mike says, presumably there is a bathroom.

    There are other errors: e.g. Item 4.20 - I doubt that SPD is fitted. There seems to be a generator. PFC = 0.2 kA on page 3 but 1.07 kA on page 8.

    ETA: the electrician was a member of the Stroma scheme, but that has been taken over by NAPIT and his details appear in their register. You may wish to contact them.

Reply
  • Day567: 
    I have attached an image of the back page of the EICR document as well as the file for the whole EICR: just to confirm you are saying that due to this being completely blank the EICR is void?

    It isn't so much void as incomplete.

    The paperwork seems to be a bit of a mongrel - it is not the current model form or the one before it. As Mike says, presumably there is a bathroom.

    There are other errors: e.g. Item 4.20 - I doubt that SPD is fitted. There seems to be a generator. PFC = 0.2 kA on page 3 but 1.07 kA on page 8.

    ETA: the electrician was a member of the Stroma scheme, but that has been taken over by NAPIT and his details appear in their register. You may wish to contact them.