Farm Outbuilding Office & TT Earthing etc.

The wild geese are migrating now. We can see them overhead flying south as they appear out of the morning mists, calling to each other as they fly in large numbers in a large V formation. Then they disappear back into the high level mists. Some say that they will fly to S. Africa.

Wild Geese Flying - Bing video

Meanwhile, a local smallholder who keeps four footed animals, has built a new wooden building to be used as an office and farm storage unit. The new proposed office is only about 25 metres square.

He asked me about installing a few sockets and lighting in the new building.

Presently the nearest supply is a plastic cased TT earthed consumer unit.

Near to the new build there are two earth electrodes used solely by the electric fencer unit. These are run in parallel. How far away from any TT L.V. installation earth electrode should they be?

Will the electric fencer interfere in any way with I.T. equipment?

Shall I supply the office with P.M.E. earthing, or shall I TT it?

I have my own thoughts on these matters, but wish not to have missed any safety issues.

There is a miniature Shetland pony that can't eat regular grass. It is allergic to it. Its hay has to be “sterilised” in a hay steamer rated at just under 3kW.

Thanks,

 

Z.

 

 

Parents
  • Zoomup: 
     

    Thanks Mike.  An office  TT earth electrode will be too close to the electric fencer electrodes for my liking. I will stick to P.M.E. just for the office. The fencer will remain TT supplied on its existing supply.

    Z.

    Provided there are no buried extraneous-conductive-parts, that is OK, otherwise the electric fence electrode would still be too close.

    There is perhaps another solution which hasn't been discussed … export TT from another building (if there's overhead on the demand) … no need for a new electrode for the second building if you also export a protective conductor from the other TT building.

Reply
  • Zoomup: 
     

    Thanks Mike.  An office  TT earth electrode will be too close to the electric fencer electrodes for my liking. I will stick to P.M.E. just for the office. The fencer will remain TT supplied on its existing supply.

    Z.

    Provided there are no buried extraneous-conductive-parts, that is OK, otherwise the electric fence electrode would still be too close.

    There is perhaps another solution which hasn't been discussed … export TT from another building (if there's overhead on the demand) … no need for a new electrode for the second building if you also export a protective conductor from the other TT building.