It’s only about eighteen weeks until the new edition of the regs is published, so whats coming?
mapj1:
no instant problem for landlords, the legislation will remain locked to the previous set of regs ;-)
The other change in the draft was a reduction to the sockets distance in bathrooms, it will be interesting if that gets to the final
Yes it is just so difficult to stretch my phone charger wire so that the charger is safely perched on the edge of the bath when I am bathing. Can't I have an electric socket by the bath?
I'd hope someone considers the larger, more complex installs when changing regulations - how are these changes going to affect a large office environment for example with multiple boards or 36 way 3 phase DBs on every floor..…….Because any change in regulations that affects a single socket say (RCDS, AFDDs, SP etc) , or a light circuit, in this type of environment gets multiplied by 10 000 for the cost of compliance; the affects of a change in regulations are felt more, be it AFDDs, RCDs, surge protection or what ever the case might be.
Good for me, but the costs are unbelievable - for what was absolutely compliant last year is suddenly going to kill everyone in the office this year because someone tried to change the regulations to make houses safer……… type thingy…..
The ol' law of unexpected consequences.
Interesting that the Wiring matters article says that amendment 2 will come into use on publication. I may be missing something but how are people supposed to design a compliant installation now (for installation in a few weeks) when the regulations are not available?
Well according to
this article on the IET website
"Amendment 2 comes into effect immediately when published on 28th March 2022 and the previous version, BS 7671:2018+A1:2020, will be withdrawn six months later."
So I read that as saying during those 6 months, you can follow either. If not, as you say, it would be impossible for anyone to go to work the day after publication.
Actually even so the changes had better be small, as 6 months is still an impractically short time in terms of big civil programmes with a significant design effort, where a year or two from drawing board to 1st fix, let alone energisation, or god forbid acceptance and sign off, is not unknown.
Oddly the draft that was for comments is still available to download.
PS
From the draft if you put a smoke detector or a lamp holder or two on the socket circuit and fit 40A MCBS for showers and cookers you can probably comply with no AFDD fitted .
Those of us with a lathe in the back bedroom are probably OK too.
And we do not know what has changed after all those comments. They cannot all have been resoundingly positive, at least one was not, as I generated that one.
421.1.7 Arc fault detection devices (AFDD) conforming to BS EN 62606 shall be provided for single-phase AC final circuits supplying socket-out lets and fixed current-using equipment with a rated current not exceeding 32 A. AFDDs conforming to BS EN 62606 are recommended for all other final circuits. AFDDs may be omitted where unexpected disconnection of the circuit could cause danger, for example:
(i) the exciter circuit of a rotating machine
(ii) the supply circuit of a lifting magnet
(iii) a circuit supplying a fire extinguishing device
(iv ) a circuit supplying a safety service, such as a fire alarm or a gas alarm
(v) a circuit supplying medical equipment used for life support in specific medical locations where an IT system is incorporated
(vi) lighting circuits in dwellings.
Where used, AFDDs shall be placed at the origin of the circuit to be protected.The use of AFDDs does not obviate the need to apply one or more measures provided in other clauses in this standard.