RCD Protection For Old Installations

Former Community Member
Former Community Member

Hey there, 

Would like to hear your thoughts on the case. 

If the installation from the 70s or 80s with old mem board has no rcd protection for neither sockets nor lights (with metal front plate switches, which are connected to CPC), taking into consideration that the installation was working cheerfully since the old days till today and all Zs values are within the range of the installed breakers and overall good condition. Would this require an upgrade to rcd protection as of the 18th edition or would class as C3 as of best practice guide 4 suggest on eicr? 

How would you approach the situation?

Regards, 

Karolis

Parents
  • Karolis Meskunas: 
     

     don`t think so the landlord is up for it.  

    The same landlord who will throw you to the wolves if there’s a complaint from the tenants or worse.

    Write up an EICR which clearly states any non-compliances with the current edition of the Wiring Regulations and add that upgrading is highly recommended.

    In light of the recent prosecution of an electrician for issuing a satisfactory EICR for a forty year old installation without raising any concerns, the idea that if it complied with the regulations forty years ago it will still be okay now has well and truly been knocked on the head.

Reply
  • Karolis Meskunas: 
     

     don`t think so the landlord is up for it.  

    The same landlord who will throw you to the wolves if there’s a complaint from the tenants or worse.

    Write up an EICR which clearly states any non-compliances with the current edition of the Wiring Regulations and add that upgrading is highly recommended.

    In light of the recent prosecution of an electrician for issuing a satisfactory EICR for a forty year old installation without raising any concerns, the idea that if it complied with the regulations forty years ago it will still be okay now has well and truly been knocked on the head.