Single phase sub-main

Evening, I'm seeking some advise pls. I have a 4core 25mm2 SWA and was going to use this for two single phase submains running from and to a common point, where the circuits will then go into separate consumer units. limited loads a garage and stable. The cable will have DP isolation and RCD protection on each circuit (2cores L+N per sub main) at the supply point. I'm also looking to run a separate earth cable of 25mm2 which would be common to both circuits and armouring of the SWA cable is also earthed and common. My question is I believe this to be complaint with 17th Ed; As I can't see anything saying its not. Second question, could I common the neutral for both submains and therefore use the fourth conductor in the SWA as an earth which would save installing the separate earth cable? Again, I can't see anything incorrect as limited loads to a couple of sockets and a few lights.  thanks for assistance. GA

Parents
  • If the distribution circuits start and finish in the same places, why not have just one circuit?

    I am not clear how you propose to terminate one cable in two CUs.

    25 sqmm seems big for “limited loads”, but perhaps the cable is very long and voltage drop is potentially an issue?

    It seems unlikely that such a large CPC will be required.

    What is the earthing system please?

Reply
  • If the distribution circuits start and finish in the same places, why not have just one circuit?

    I am not clear how you propose to terminate one cable in two CUs.

    25 sqmm seems big for “limited loads”, but perhaps the cable is very long and voltage drop is potentially an issue?

    It seems unlikely that such a large CPC will be required.

    What is the earthing system please?