Evening, I'm seeking some advise pls. I have a 4core 25mm2 SWA and was going to use this for two single phase submains running from and to a common point, where the circuits will then go into separate consumer units. limited loads a garage and stable. The cable will have DP isolation and RCD protection on each circuit (2cores L+N per sub main) at the supply point. I'm also looking to run a separate earth cable of 25mm2 which would be common to both circuits and armouring of the SWA cable is also earthed and common. My question is I believe this to be complaint with 17th Ed; As I can't see anything saying its not. Second question, could I common the neutral for both submains and therefore use the fourth conductor in the SWA as an earth which would save installing the separate earth cable? Again, I can't see anything incorrect as limited loads to a couple of sockets and a few lights.  thanks for assistance. GA

Parents
  • Quite often in farm type installations a 300mA R.C.D. is installed at the origin of a sub-main. This then allows earth faults to disconnect without the need for large “long duration” fault currents to open protective devices. This offers fire protection. An “S” type or time delayed R.C.D. can be used at the origin, and instant 30mA types for say sockets for the final circuits.

    705.422.7

    Z.

Reply
  • Quite often in farm type installations a 300mA R.C.D. is installed at the origin of a sub-main. This then allows earth faults to disconnect without the need for large “long duration” fault currents to open protective devices. This offers fire protection. An “S” type or time delayed R.C.D. can be used at the origin, and instant 30mA types for say sockets for the final circuits.

    705.422.7

    Z.

Children
No Data