Overhead cable suitability for cat wire

Looked at a job for a customer and the cable supplying the shed in their garden is a pvc T&E about 5 m up spanning about 5 metres. There's some sort of catenary wire (looks like a bit of old fencing wire) and its snapped so the cable is holding the wire up. I'm going to replace it but wondered whether NYY-J cable would be considered suitable rather than SWA? it's lighter and seems to be widely considered fine for outdoor use, and is obviously quicker to joint. SWA is obviously stronger but if the cat wire does its job properly would the cable itself require mechanical protection? I cant find a reg?

Parents
  • At the risk of stating the obvious

    Also remember that 521.10.202 now applies to all wiring systems … so no relying on nylon cable ties to support the cable from the catenary wire.

    I can see that the old school approach of a few turns of insulating tape followed by a couple of turns of thin wire, ends twisted together, might see a resurgence.

       - Andy.

Reply
  • At the risk of stating the obvious

    Also remember that 521.10.202 now applies to all wiring systems … so no relying on nylon cable ties to support the cable from the catenary wire.

    I can see that the old school approach of a few turns of insulating tape followed by a couple of turns of thin wire, ends twisted together, might see a resurgence.

       - Andy.