Inspection & Testing

I am a project manager, constructing new waste water treatment works, for a water company. The contractor building the new works has provided a program which has 4 months between  part 1 (dead testing) and part 2 (live testing) of the NICIEC certification. In between these dates, the contractor will test and commission of the plant and equipment e.g. pumps, actuated valves, instrumentation, screens etc.

Would it be correct to say, this does not comply with the wiring regulations ? 

Parents
  • I think that it is very much in compliance.

    641.1 Every installation shall, during erection and on completion before being put into service, be inspected and tested to verify, so far as is reasonably practicable, that the requirements of the Regulations have been met.

    Difficult to see how live tests could be undertaken much before commissioning, but performing dead tests as cables, etc. are installed enables corrective action to be taken at the earliest opportunity.

Reply
  • I think that it is very much in compliance.

    641.1 Every installation shall, during erection and on completion before being put into service, be inspected and tested to verify, so far as is reasonably practicable, that the requirements of the Regulations have been met.

    Difficult to see how live tests could be undertaken much before commissioning, but performing dead tests as cables, etc. are installed enables corrective action to be taken at the earliest opportunity.