Advice on trench depth for SWA - Answered!

I'm planning to build a timber garden room for use as an amateur radio shack. It will have a TT mains supply from the house consumer unit. I can't attach the SWA to a fence as the boundary belongs to the neighbour so it will have to go underground.

The trench will be about 5 metres long under a gravel walkway and will cross a sewer pipe that is 600mm below the surface with an inspection cover nearby. How deep does the trench need to be?

Mike

Parents
  • I've just seen a video on youtube where an electrician ran SWA across a garden path by cutting a channel in it. Surely that's not allowed?

    The regulations often really aren't as simple as something ‘is allowed’ or ‘is not allowed’. There has been a definite trend over more recent years to move away from a rigid list of things to do and avoid, and more towards what needs to be achieved - leaving the designer with much more scope to so what's sensible in any particular situation.

    In a way that's illustrated by the very title of the wirings regs. Back in the 1st Ed the wiring regs were called “Rules and Regulations” - and the Victorians had very specific ideas about the differenence between a Rule and a Regulation - a Rule demanded or prohibited (i.e. was a ‘thou shalt’ or ‘thou shalt not’) whereas a Regulation merely put conditions on things ( ‘xyz may be done on any day excepting the Sabbath’).  By the 8th Ed the word “Rules” had disappeared forever from the title.

    There might even be situations - perhaps when running a cable over a bridge or some layered foundations - that cutting a shallow trench in the thin non-structural surface layers is a far better idea than going deeper. A simple set of rules really can't cover every situation.

       - Andy.

Reply
  • I've just seen a video on youtube where an electrician ran SWA across a garden path by cutting a channel in it. Surely that's not allowed?

    The regulations often really aren't as simple as something ‘is allowed’ or ‘is not allowed’. There has been a definite trend over more recent years to move away from a rigid list of things to do and avoid, and more towards what needs to be achieved - leaving the designer with much more scope to so what's sensible in any particular situation.

    In a way that's illustrated by the very title of the wirings regs. Back in the 1st Ed the wiring regs were called “Rules and Regulations” - and the Victorians had very specific ideas about the differenence between a Rule and a Regulation - a Rule demanded or prohibited (i.e. was a ‘thou shalt’ or ‘thou shalt not’) whereas a Regulation merely put conditions on things ( ‘xyz may be done on any day excepting the Sabbath’).  By the 8th Ed the word “Rules” had disappeared forever from the title.

    There might even be situations - perhaps when running a cable over a bridge or some layered foundations - that cutting a shallow trench in the thin non-structural surface layers is a far better idea than going deeper. A simple set of rules really can't cover every situation.

       - Andy.