Double insulated single core cable on outside of house to resolve earth bonding

Hi I have to resolve an earth bonding issue where the incoming water supply pipe is cast iron and enters the house on the opposite side to the CU.

It's sold floors, beams showing although there may be a roof void but the easiest way is round the outside. I am considering using 10mm or 16m single core double insulated cable, blue or brown sleeved to green/yellow.

 

I am looking at this as a conduit run is a bit unsightly and takes time, just thinking there must be a better solution. Whats your opinion on the solution and any other ideas?

Thanks

 

Alan

  • Alan B: 
     

    Hi I have to resolve an earth bonding issue where the incoming water supply pipe is cast iron and enters the house on the opposite side to the CU.

    It's sold floors, beams showing although there may be a roof void but the easiest way is round the outside. I am considering using 10mm or 16m single core double insulated cable, blue or brown sleeved to green/yellow.

     

    I am looking at this as a conduit run is a bit unsightly and takes time, just thinking there must be a better solution. Whats your opinion on the solution and any other ideas?

    Thanks

     

    Alan

    What is wrong with running green and yellow 10.mm2 single clipped direct on the outside wall using the best route for neatness? I have seen lots of 10.0mm2 green and yellow run on surface brickwork externally. Sometimes the cable can be hidden behind rainwater downpipes, run high or low as required.

    Z.

  • Agree that single covered green/yellow should be fine. The pvc covering will eventually degrade by exposure to sunlight, but that wont impair the integrity of the bonding connection.

    Even after decades I would expect that enough of the green/yellow pvc would remain so as to make the purpose of the conductor clear.

  • If G/Y isn't aethetically pleasing, I might think about conduit - either rigid or small flexible conduit - that can relatively quick to fix around bends and made to stay straight if installed a little tight. Since you probably shouldn't be using plastic hammer-in clips these days anyway, there's probably not a huge difference in time between installing P-clips and saddles.

       - Andy.

  • All thanks for your suggestions. I will give the customer the choice of just the cable or run it in conduit. I will probably use  linian super clips to make a neat job of it.

  • Alan B: 
     

    All thanks for your suggestions. I will give the customer the choice of just the cable or run it in conduit. I will probably use  linian super clips to make a neat job of it.

    Only needed in my opinion if the cable is to be affixed at high level and may impede egress in case of fire or other emergency inside a building. Outside it is not so much of a problem, especially if clipped at low level.  I think that the worry in a fire is “premature collapse”.

    521.10.202

     

    Edit. Add.  Oh!, and never give customers too many option choices  as it can confuse them. Two options is plenty. Normally customers are looking for a neat job and an acceptable price. If you overestimate you may lose a job. “Keep it simple” often wins work.

     

    Z.

  • Is it not possible to stick some kind of plastic insert on the pipe where it enters?