Please settle a debate...

Is there any reason a circuit fed in t&e, protected by an RCBO,  can not be clipped to a accessible surface feeding a socket

Parents
  • No. Unless it is not suitable for the External Influences  set out in appendix 5 of BS 7671.

     

    JP

Reply
  • No. Unless it is not suitable for the External Influences  set out in appendix 5 of BS 7671.

     

    JP