The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

External RCD/sockets

Former Community Member
Former Community Member

From a house ring main can an external rcd socket be used as a fused spur to a small consumer unit in a garage less than 10m away using 2.5 buried protected cable?  (2 LED strip lights and 4 double sockets in the garage)

Parents
  • Former Community Member
    0 Former Community Member

    Thanks but What caveats? Im coming off a kitchen socket (Not Cooker) to supply the external RCD socket I then want to spur the 2.5 cable to the garage to a small consumer unit.  Will the external socket trip if the garage has an earth or mains short?

Reply
  • Former Community Member
    0 Former Community Member

    Thanks but What caveats? Im coming off a kitchen socket (Not Cooker) to supply the external RCD socket I then want to spur the 2.5 cable to the garage to a small consumer unit.  Will the external socket trip if the garage has an earth or mains short?

Children
No Data